我有一个实际应用题亟待有人参与讨论指点: ++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++ 6KV某段母线电源来自6.3KV(如图)(经611开关、电抗器、612开关) 6kv 6.3kv 电抗器 │ ┠─□─@──□─┨ 611 612 │ 6kv该段负荷有:给水泵1台(290KW In=33.7A) 启动系数Kq=6
++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
6KV某段母线电源来自6.3KV(如图)(经611开关、电抗器、612开关)
6kv
6.3kv 电抗器 │
┠─□─@──□─┨
611 612 │
6kv该段负荷有:给水泵1台(290KW In=33.7A) 启动系数Kq=6
吸风机1台(280KW In=35A) 启动系数Kq=5
送风机1台(280KW In=36.5A) 启动系数Kq=6
变压器2台(800KVA In=73.3A) 启动系数Kq=1.5
请问该段电源611开关的过流整定值怎样计算呢?
+++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
我看到有一种计算方法是先算出各负荷的总启动容量和总额定容量,两者之商为综合启动倍数Kzq,
再代到公式Idz.bh=Kk*Kzq/Kfh*In中计算。而实际启动各负荷的情况是一台一台启动,最后启动送风机。
哪位前辈能指教一二,晚生这里有礼了!
++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++